been computed as 4.95 percent. This leaves 6.00 - 4.95 = 1.05 percent voltage drop
allowed for group V.
From figure 9, attached memorandum, a 1.05 percent voltage
drop, a 1.65 KVA demand load, and a 308-foot equivalent distance require a wire
size somewhat smaller than No. 8.
However, a No. 8 wire is the smallest size
allowed for use in this project. The actual voltage drop for this branch will be
0.7 percent.
2-5