both generators are operating. Three 45 KW generators have a capacity of 135 KW,
less than the required generator capacity. Three 100 KW generators will not only
provide the required capacity, but will do it when the largest generator is out of
17. Location A is too far from the heavier loads (machine shop) to keep wire size
and amount to reasonable values. Locations B, C, and D are satisfactory from the
standpoint of being near the heaviest demand load, but location B would result in a
noise nuisance to the chapel while location D is near a storage area for flammable
products. Hence, locate the generator at location C.
1-3